[TRNSYS-users] have a problem with modeling a wall

via TRNSYS-users trnsys-users at lists.onebuilding.org
Thu Jun 29 07:06:58 PDT 2017


Hi,

You can try to compose your own wall by adjusting layers thickness in 
order to reach the R-value you're asking for. However, there's a lack of 
information : the thermal capacity of your wall.
Without it, you could have an infinite amount of solution depending on 
your wall composition.
so I would say no, the answer is that you can't model the wall only with 
the R-value.

Regards

Wirich


Le 2017-06-27 17:44, S.O.Daei.N via TRNSYS-users a écrit :
> Hi
> I want to model the attach wall with TRNBUILD,but i have no detail on
> structure of that wall.
> The only thing i have from the wall is R-value of it, is there any
> chance that i could model this wall in TRNBUILD with just R-value?
> Please help me with this problem.
> Thanks