[TRNSYS-users] Simultaneous heating and cooling operation of a ground source heat pump
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Fri Jun 23 09:30:48 PDT 2017
Stephanie,
Yes, it is possible and there is nothing special that you need to do.
When the heat pump is in "heating" mode then its load side will be
heated and the source side will be cooled. A ground source heat pump is
usually one that has air on the load side and water on the source side.
The "heating" and "cooling" describes what happens on the load side.
However, the opposite always happens on the source side.
kind regards,
David
On 06/23/2017 08:33, S. Loizide via TRNSYS-users wrote:
> Dear All,
>
> I was wondering whether it is possible to model the simultaneous
> heating and cooling operation of a ground-source heat pump in TRNSYS
> by using the heat pump component Type 927. The heat pump that I'm
> trying to model provides space heating to a building during winter but
> at the same time provides cooling to some server and paper archive
> rooms. Is it possible to have both the cooling and heating modes on by
> using this particular component (type 927)? If not, could you please
> suggest any other possible way of modelling the simultaneous heating
> and cooling operation of a heat pump?
>
> Regards,
>
> Stephanie
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
More information about the TRNSYS-users
mailing list