[TRNSYS-users] Controler Advice for evaluating Solar Radiation?
Jeff Thornton via TRNSYS-users
trnsys-users at lists.onebuilding.org
Fri Jun 2 06:52:00 PDT 2017
Javier,
Since the value you are watching won't change with the control decision, you don't need a controller with hysteresis. I would simply use an equation:
Glim = 1000
On_Controller = GE(IncidentRadiation,Glim)
where the incident radiation is an input to the equation component.
Jeff - TESS
Sent from my iPhone
> On Jun 2, 2017, at 8:27 AM, Javier Vega via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
>
> Hello TRNSYS users,
>
> I want to set a control strategy for my system based on the amount of solar radiation on a certain surface. It is simple, if the total radiation on the surface is below a Glim, I need the controller to output 1. If the total solar radiation is above Glim, set 0. The controller output will be used to divide a certain flow.
>
> Which controller would you recommend? Is the differential controller Type 2d (Generic) convenient for this case? I'm using the succesive substitution method.
>
> Thanks in advance for your advice,
> Javier Vega