[TRNSYS-users] TRNSYS 3D import in Simulation Studio fails
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Fri Jun 23 09:33:57 PDT 2017
Arnaud,
Try opening TRNBuild and selecting "Import Trnsys3D..." from the
"file" menu. You should then be able to save the imported *.idf as a
*.b18 (or *.b17) file depending on which version of TRNSYS you are using.
The "no outputs specified" error usually happens if you try to link a
Type56 proforma to a *.b18 (or *.b17) file that doesn't exist.
kind regards,
David
On 06/22/2017 08:58, Arnaud Candaele via TRNSYS-users wrote:
> Hello,
>
> I'm having difficulties importing an idf file created from the
> Sketchup addon for TRNSYS into TRNBUILD (directly, or via Simulation
> Studio).
>
> I create a simple 1 rectangular zone model in Sketchup, then save the
> idf file.
> Then I create a new 3D Building projet in Simulation Studio, and
> select the idf. I got the error message "/no OUTPUT's specified/" -
> "/please add at least one OUTPUT/".
>
> I never had that kind of problem in the past, from what I recall. But
> I was using another version on Sketchup, can it be the source of the
> problem? I am now using Sketchup Pro *2017*.
>
> Thanks a lot for any help,
> Arnaud.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170623/d72c9bab/attachment.htm>
More information about the TRNSYS-users
mailing list