Mohamed,
There are two ways that you can do it. If you are trying to model a
tempering valve (a device that prevents one stream of liquid from
overheating by mixing in some colder liquid) then you can use Type11.
Look in the 04-MathematicalReference manual and it will give you an
example of how to model it.
If you have a more general case and you want to know in what ratio to
mix the liquids to obtain a certain mixed temperature then the ratio can
be computed based on knowing the temperatures. Once you solve the
mathematics, you can then implement them as an equation in your input
file. Use the ratio as the control signal to a mixing valve model.
kind regards,
David
On 05/31/2017 02:26, Mohamed Kaheal via TRNSYS-users wrote:
> Hello TRNSYS team,
>
> I would like to mix two streams of fluids. the temperature of the
> fluids are known. the flow rate of the first stream is fixed. I need
> to take part of the second stream to mix it with the first stream in
> order to reach to some specific temperature values. Could you please
> tell me how can I do that. Any help will be appreciated
>
>
> Thanks a lot
> Mohamed
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170602/4b877700/attachment.htm>
More information about the TRNSYS-users
mailing list