[TRNSYS-users] Problem in running the program
    David BRADLEY via TRNSYS-users 
    trnsys-users at lists.onebuilding.org
       
    Mon Jul 17 12:25:16 PDT 2017
    
    
  
It means that your system is experiencing conditions that are not 
physically possible. The problem could be from Type56 (TRNBuild is an 
interface for generating Type56 files) or it could be originating in one 
of the system components. I would recommend that you temporarily 
disconnect the flow of air into the building but leave the exhaust flow 
connected. Using a Type65, watch the temperature, RH, and flow rate of 
air through each of the components in the system as it proceeds from 
ambient conditions to the conditions that are being supplied to the 
building. You should be able to get a clearer idea what is happening to 
the air and where the problem lies.
kind regards,
  David
On 07/15/2017 08:59, S.O.Daei.N via TRNSYS-users wrote:
> Hi there
> I have problem with my project
> I get this error, what is that mean?
> Is that related to my house simulation on TRNBUILD?
>  ***** ERROR *****        TRNSYS ERROR # 116
>  UNIT  14 TYPE 505
>  THE PSYCHROMETRICS SUBROUTINE WAS CALLED WITH CONDITIONS
>  YIELDING A SATURATION PRESSURE GREATER THAN  AMBIENT PRESSURE
>
>
>  ***** ERROR *****        TRNSYS ERROR # 116
>  UNIT  64 TYPE 667
>  THE PSYCHROMETRICS SUBROUTINE WAS CALLED WITH CONDITIONS
>  YIELDING A SATURATION PRESSURE GREATER THAN  AMBIENT PRESSURE
> Please help me
> regards,
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170717/de9675f5/attachment-0001.htm>
    
    
More information about the TRNSYS-users
mailing list