[TRNSYS-users] Error IDF import in TRNBuild

David BRADLEY via TRNSYS-users trnsys-users at lists.onebuilding.org
Thu Jan 26 08:06:15 PST 2017


Issmail,

  I have not found a very easy way to determine which surface is the 
problem. Usually what I do is to accept the error shown in your screen 
capture, then go to the zone in which the adjacent wall is not found. 
Find the wall in question and note its area. Then close TRNBuild, return 
to SketchUp/Trnsys3D, go to the same zone and look for a wall that has 
the same area. Once you have verified that it is set up correctly, go to 
the zone to which that wall is adjacent and find the same surface. 
Verify its information as well.

kind regards,

  David



On 01/25/2017 12:04, Issmail OUHALLOU via TRNSYS-users wrote:
> Dear Trnsys users,
>
> How to correct quickly the following error? Otherwise, how to find the 
> surface in question?
>
>
>> Please note, I've checked all surfaces but didn't find which one 
> presents the error...
> Thanks.
>
> Regards,
> Ismail
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170126/fecdbb14/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 62908 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170126/fecdbb14/attachment-0001.png>


More information about the TRNSYS-users mailing list