[TRNSYS-users] problem with differential controller

Jeff Thornton via TRNSYS-users trnsys-users at lists.onebuilding.org
Sat Apr 29 08:52:42 PDT 2017


Amirreza,

Real solar collectors do the same thing under certain circumstances.  From a first glance I would say your dead bands are too tight - typically we see 10/2 not 5/2.  It's also possible that your collector pump flow rate is  too high.  With collectors connected in series you typically have a pump flow rate the same as if you had only one collector.  Collectors are designed for a given maximum flow rate for pressure drop reasons.  For example, assume we had a collector that wanted 450 kg/h of flow and we had 6 in series.  We would run the pump at 450 (each collector gets the 450 that way).  You wouldn't run your pump at 2700 (450 x 6) or the pressure drop would be ridiculously high.  If you have that high of a flow rate you'll get exactly what you are seeing in your project.  With no flow the collector temperature is above the deadband but when the pump turns on the high flow rate causes the outlet temperature to drop below the lower deadband.  The controller can't find a solution since both are correct and will oscillate between on and off.

Jeff
TESS Inc

Sent from my iPhone

> On Apr 29, 2017, at 2:36 AM, Amirreza Heidary via TRNSYS-users <trnsys-users at lists.onebuilding.org> wrote:
> 
> Dear All
> I'm using a 5 collectors in series with a differential controller to turn on the pump when the difference of collector outlet and inlet temperatures is more than 5 and turn it off when it is less than 2.But the signal and collector output temperatures are fluctuating too much, also the signal is not compatible with temperature variations.as you can see in the following diagram, the signal is 1 when the outlet temperature is at maximum ! 
> (red line is collector outlet temperature and orange line is the controller signal)
> 
>  
> 
> --------------------------------------------------------------------------------------------------------------------------------------------------
> 
> amirrezaheidary
> master student of energy systems Engineering
> Sharif university of technology
> Tehran-Iran
> E-mail address:
> heidari at energy.sharif.edu
> 
> amirrezaheidarysbu at gmail.com
> 
> P Save a tree... Please don't print this E-mail unless you really need to.                                                                                                                              
> 
> 
> 
> 
> 
> 
> 
>    Sent with Mailtrack
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/156dff6f/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 305835 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/156dff6f/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 24253 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/156dff6f/attachment-0007.png>


More information about the TRNSYS-users mailing list