Hi Amirreza,
I am no expert but I would try to run the simulation with a much smaller
timestep. Furthermore if the collectors have no thermal capacitance this
control system is likely to be unstable and oscillate. Try using a
temperature from the tank into the controller.
Regards
Oriol Casal
On Apr 29, 2017 09:36, "Amirreza Heidary via TRNSYS-users" <
trnsys-users at lists.onebuilding.org> wrote:
> Dear All
> I'm using a 5 collectors in series with a differential controller to turn
> on the pump when the difference of collector outlet and inlet temperatures
> is more than 5 and turn it off when it is less than 2.But the signal and
> collector output temperatures are fluctuating too much, also the signal is
> not compatible with temperature variations.as you can see in the
> following diagram, the signal is 1 when the outlet temperature is at
> maximum !
> (red line is collector outlet temperature and orange line is the
> controller signal)
> [image: Inline image 1]
> [image: Inline image 2]
>
> ------------------------------------------------------------
> ------------------------------------------------------------
> --------------------------
>
> *amirrezaheidary*
> *master student of energy systems Engineering*
> *Sharif university of technology*
> *Tehran-Iran*
> *E-mail address*:
>
> heidari at energy.sharif.edu
>
> a <sm_mousavi at pwut.ac.ir>mirrezaheidarysbu at gmail.com
>
> *P* *Save a tree... Please don't print this E-mail unless you really need
> to.*
>
>
>
>
>
>
>
>
> <https://mailtrack.io/> Sent with Mailtrack
> <https://mailtrack.io/install?source=signature&lang=en&referral=amirrezaheidarysbu@gmail.com&idSignature=22>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/2808530d/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 24253 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/2808530d/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 305835 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170429/2808530d/attachment-0003.png>
More information about the TRNSYS-users
mailing list