[TRNSYS-users] how to account number of hours which temperature is out of range?
David BRADLEY via TRNSYS-users
trnsys-users at lists.onebuilding.org
Wed Apr 12 20:33:52 PDT 2017
you can use an equation that compares the greenhouse temperature to a
scheduled value (set by a Type14) and sets a value of 1 if the
greenhouse temperature goes out of bounds.
alternatively there is a Type584 in the TESS Utility library (Zone
temperature watcher) that is designed to do just what you need.
best,
David
On 04/12/2017 07:15, Amirreza Heidary via TRNSYS-users wrote:
> Dear All
> I have designed a cooling system for a greenhouse. The temperature
> should be between 22 and 28 C during the day and 15 to 21 C during
> the night. I'm going to account number of hours during a month, which
> the greenhouse temperature is out of the range. As the standard range
> of temperature is different during the day and night, how can I
> calculate it?
> Thank you
>
> --------------------------------------------------------------------------------------------------------------------------------------------------
>
> *amirrezaheidary*
> /master student of energy systems Engineering/
> /Sharif university of technology/
> /Tehran-Iran/
> /E-mail address/:
>
> heidari at energy.sharif.edu <mailto:heidari at energy.sharif.edu>
>
> a <mailto:sm_mousavi at pwut.ac.ir>mirrezaheidarysbu at gmail.com
> <mailto:mirrezaheidarysbu at gmail.com>
>
> *P*//*/Save a tree... Please don't print this E-mail unless you really
> need to./***
>
>
>
>
>
>
>
> <https://mailtrack.io/> Sent with Mailtrack
> <https://mailtrack.io/install?source=signature&lang=en&referral=amirrezaheidarysbu@gmail.com&idSignature=22>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20170412/fa20bd50/attachment.htm>
More information about the TRNSYS-users
mailing list