Antoine,
   This is a common source of confusion. Two points are important to 
keep in mind. First, the collector array area parameter is the area of 
the entire array, not just the area of one module in the array. Second, 
if you add a second collector you have to be careful about what you do 
with the flow rate. If you are adding a second collector in parallel to 
the first one you should double the collector array area, leave the 
"number in series" parameter set to 1, and double the liquid flow rate 
to the array. If you are adding a second collector in series with the 
first one, you should double the collector array area, set the number in 
series to 2, and leave the liquid flow rate unchanged.
kind regards,
  David
On 10/20/2016 11:46, Antoine Gautier via TRNSYS-users wrote:
>
> Hi
>
> I cannot figure out why the number of collectors in series has no 
> effect on the collectors array efficiency: see attached project.
>
> Computing equations from source code manually I would state the opposite…
>
> Thanks for your help.
>
> Best regards
>
> --
>
> Antoine Gautier
>
> Solamen
>
> +33 6 58 24 02 60
>
> antoine.gautier at solamen.fr
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161020/92ec8739/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list