[TRNSYS-users] TRNSYS counter function
Angel Carrera via TRNSYS-users
trnsys-users at lists.onebuilding.org
Mon Nov 14 01:54:40 PST 2016
Hi,
not sure if I understood right, but I think I use the input value recall
for essentially the same problem: pass the condition (heat and ambient
temperature under your limit) to type 93 as a 0/1, and sum the outcome of
the number of time steps necessary to reach "a certain time". If the sum is
equal to the required value, trigger the defrost condition. Hope it helps,
regards
Angel
2016-11-13 4:17 GMT+01:00 via TRNSYS-users <
trnsys-users at lists.onebuilding.org>:
> Hello everyone,
>
> I am trying to figure out a way to model a defrost timer on as air source
> heat pump. To do so, I would have to set up a counter that would activate a
> defrost cycle (force heat pump into cooling mode) after the heat pump has
> been working in heat mode and the outside temperature is below a certain
> limit for a certain amount of time.
>
> I have tried using Type 1233, but this component does not wait before
> triggering the output, it rather starts right away when the conditions are
> met, then is stuck in OFF position for a certain amount of time.
>
> Any help with this issue would be appreciated.
>
> Thanks!
>
> Olivier Quevillon
>
> Étudiant à la maîtrise en Génie Mécanique
> École de Technologie Supérieure
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
--
Àngel Carrera Martín
Consultor sènior en Sistemes
Llicenciat en ciencies físiques
Sistemes Avançats d'Energia Solar Tèrmica - AIGUASOL
+(00) 34 663 276 680 Roger de Llúria 29, 3r 2a
*angel.carrera at aiguasol.coop* <angel.carrera at aiguasol.coop> 08009
Barcelona
angel_aiguasol Tel: (+34) 933 424 755
www.aiguasol.coop
<http://www.aiguasol.coop/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161114/cef06251/attachment-0003.htm>
More information about the TRNSYS-users
mailing list