[TRNSYS-users] question about TABS
hotline via TRNSYS-users
trnsys-users at lists.onebuilding.org
Mon Nov 7 07:12:29 PST 2016
Dear XuCe,
there is no other option than splitting your ceiling into surfaces with and surfaces without TABS if you want to to have this high degree of accuracy. But make sure that you define only concave surfaces without wholes (you did it correct in your drawing on the right side)
Best
Jakob
_________________________________________________________________________________________________
Jakob Merk
TRNSYS Software Team
Transsolar Energietechnik GmbH
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von Physic&Energy via TRNSYS-users
Gesendet: 07 November 2016 11:50
An: trnsys-users
Betreff: [TRNSYS-users] question about TABS
Dear all,
For studying the tabs system, we learn a lot about it. One book “TABS Control” said the actual laying area has a certain effect on the indoor temperature. So in order to accurately simulating the actual running situation of tabs system, we need to keep the laying area, inlet mass flow, inlet water temperature and pipe spacing exactly the same as the actual project.
We create zones in sketchup. For example there are two floors and I want to put the tabs system on the ceiling of the ground floor. The actual laying area is smaller than the area of the zone because of the beam and column.
We have an idea that dividing the floor into two parts- one part is equal to the laying area (the center of the ceiling) and the other part is the rest of the floor. But we think this method is much too complicated and not the right way to solve it. So how do we deal with the problem? Is there a better way?
[cid:image001.png at 01D23911.BC9AE220] [cid:image002.png at 01D23911.BC9AE220] [cid:image003.png at 01D23911.BC9AE220] [cid:image004.png at 01D23911.BC9AE220]
Best Regards
XuCe
------------------
[http://a2.qpic.cn/psb?/f5c203e3-7585-4f7b-ae8d-efb6a67c579a/4rRUJTohYAZWTeBUOnjAcmTVr4dtoZQnM*2zFj2eg90%21/b/dA0BAAAAAAAA&ek=1&kp=1&pt=0&bo=IQQJASEECQEDCC0%21&sce=60-2-2&rf=viewer_311]<http://www.dsfzh.com/>
技术研发中心
Technology R & D Center
建筑物理与能源设计研究所
Building Physics & Energy Design Institute
T +86 (411) 3966 2559
F +86 (411) 3966 2566
W www.dsfzh.com<http://www.dsfzh.com>
大连都市发展设计有限公司
Dalian Urban Development Design Co.,Ltd
116011 大连市西岗区长春路186号
No. 186 Changchun Road, Xigang District, Dalian
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161107/bfc613fb/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25142 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161107/bfc613fb/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 19415 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161107/bfc613fb/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23589 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161107/bfc613fb/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 22991 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161107/bfc613fb/attachment-0015.png>
More information about the TRNSYS-users
mailing list