Amaury,
As far as I am aware, hot water fired absorption chillers always have
three water steams: the hot water stream that provides the energy that
drives the cycle, the chilled water stream that is cooled by the cycle
and a cooling water stream that is connected to an energy sink (cooling
towers or a heat exchanger) for energy rejection from the two condensers
in the cycle. Have a look at:
http://goldman.com.au/energy/company-news/how-does-an-absorption-chiller-work/
kind regards,
David
On 11/20/2016 10:39, amaury.tenaille at epfedu.fr via TRNSYS-users wrote:
>
> Hello,
>
>
> I have to modelise a system of cooling and heating with solar panel
> using an absoption chiller.
>
> My problem is that the absorption chiller on TRNSYS have 2 inlet
> fluids, one cold and one hot. My system only need one, heated by the
> solar panel. Can I fing one like that or how can I change the one with
> 2 inlet fluid ?
>
> Thank you very much for your help.
>
>
> Amaury
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161121/c4a3422a/attachment.htm>
More information about the TRNSYS-users
mailing list