[TRNSYS-users] Absorption chiller

David BRADLEY via TRNSYS-users trnsys-users at lists.onebuilding.org
Mon Nov 21 11:47:14 PST 2016


Amaury,

   As far as I am aware, hot water fired absorption chillers always have 
three water steams: the hot water stream that provides the energy that 
drives the cycle, the chilled water stream that is cooled by the cycle 
and a cooling water stream that is connected to an energy sink (cooling 
towers or a heat exchanger) for energy rejection from the two condensers 
in the cycle. Have a look at:

http://goldman.com.au/energy/company-news/how-does-an-absorption-chiller-work/

kind regards,

  David



On 11/20/2016 10:39, amaury.tenaille at epfedu.fr via TRNSYS-users wrote:
>
> Hello,
>
>
> I have to modelise a system of cooling and heating with solar panel 
> using an absoption chiller.
>
> My problem is that the absorption chiller on TRNSYS have 2 inlet 
> fluids, one cold and one hot. My system only need one, heated by the 
> solar panel. Can I fing one like that or how can I change the one with 
> 2 inlet fluid ?
>
> Thank you very much for your help.
>
>
> Amaury
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20161121/c4a3422a/attachment.htm>


More information about the TRNSYS-users mailing list