[TRNSYS-users] Question on Type 15-1 (TMY Weather file)
David BRADLEY
d.bradley at tess-inc.com
Mon Mar 7 20:22:35 PST 2016
Mohammad,
My apologies for the delay in getting back to you. You can use
instances of Type11 to mix two flows into a single flow before passing
it to the heat pump. You can then use another instance of Type11 to
split the flow from the heat pump back to the two tanks.
kind regards,
David
On 03/01/2016 14:01, MOHAMMAD MATARNEH wrote:
> Mr. David Bradley;
>
> thank you very much but how also can i make the heat pump(water -water
> heat pump) to take 2 sources of water from 2 separated storage tanks?
> and what type of heat pump does support that?
>
> best regards.
>
>
> On Monday, February 29, 2016 4:58 PM, David BRADLEY
> <d.bradley at tess-inc.com> wrote:
>
>
> Mohammad,
> The simplest way would be to define two equations one of which has a
> value of 1 during the time period when you want to allow cooling and
> the other of which has a value of 1 during the heating time period.
> For example:
>
> isSummer = AND(GT(TIME,3000),LT(TIME,5000))
> isWinter = 1-isSummer
>
> You then connect the result of these equations to the appropriate heat
> pump inputs. The above equations would allow cooling between hour 3000
> and 5000 of the simulation and would allow heating at all other times.
> You have to be a bit more careful with your equation if you want to
> run multiyear simulations.
> kind regards,
> David
>
>
> On 02/28/2016 14:26, MOHAMMAD MATARNEH wrote:
>> dear all ;
>>
>> how can i control run this circled heat pump to work on heating mode
>> in winter and cooling mode in summer.
>>
>> best regards
>>
>>
>> On Monday, February 22, 2016 6:06 PM, Eirini Mantesi
>> <E.Mantesi at lboro.ac.uk> <mailto:E.Mantesi at lboro.ac.uk> wrote:
>>
>>
>> Hi Jakob,
>>
>> Thank you for your prompt response.
>>
>> Unfortunately, both the restaurant and the sunspace examples use Type
>> 15-6 and Type 15-2 (TMY-2). My problem is that when I replace to
>> Type 15-1 (TMY), my heating demand is increased, but remains within
>> the BESTEST range, while my cooling demand is significantly below the
>> BESTEST results. That's how I concluded that most probably I am doing
>> something wrong in the connection of the weather file and the solar
>> radiation available in the building's surfaces.
>>
>> Thank you for your help anyway.
>>
>> Kind Regards,
>> Eirini
>>
>> Eirini Mantesi
>> Research Engineer
>> School of Civil and Building Engineering
>> Loughborough University
>> T: +447462665904
>> E: E.Mantesi at lboro.ac.uk <mailto:E.Mantesi at lboro.ac.uk>
>>
>>
>> ------------------------------------------------------------------------
>> *From:* TRNSYS-users <trnsys-users-bounces at lists.onebuilding.org>
>> <mailto:trnsys-users-bounces at lists.onebuilding.org> on behalf of
>> hotline <hotline at Transsolar.com> <mailto:hotline at Transsolar.com>
>> *Sent:* Monday, February 22, 2016 3:46 PM
>> *To:* TRNSYS users mailing list at OneBuilding.org
>> *Subject:* Re: [TRNSYS-users] Question on Type 15-1 (TMY Weather file)
>> Dear Eirini,
>> you can find an example in your TRNSYS directory under
>> …\Examples\Restaurant\Restaurant.tpf
>> It also uses types 15 and 56…
>> Best regards
>> Jakob Merk
>> _________________________________________________________________________________________________
>> /Jakob Merk/
>> TRNSYS Software Team
>> /
>> /*Transsolar Energietechnik GmbH*
>> Curiestraße 2
>> 70563 Stuttgart
>> Fax: +49 711 67976-45
>> Email: hotline at transsolar.com <mailto:hotline at transsolar.com>
>> Web: www.trnsys.de <http://www.trnsys.de/>
>> *Von:*TRNSYS-users
>> [mailto:trnsys-users-bounces at lists.onebuilding.org] *Im Auftrag von
>> *Eirini Mantesi
>> *Gesendet:* Montag, 22. Februar 2016 16:43
>> *An:* TRNSYS users mailing list at OneBuilding.org
>> *Betreff:* [TRNSYS-users] Question on Type 15-1 (TMY Weather file)
>> Hello TRNSYS Users,
>> I am trying to simulate a simple building (BESTEST Case 600) and I am
>> getting quite odd results. I believe that my mistake is in the
>> connection between Type 15-1 (TMY Weather file) and Type 56
>> (Multi-zone building). I would like to ask whether there is any
>> tutorial online or any example in the program's documentation
>> folder on how to connect weather files to Type 56 for multi-zone
>> building simulation.
>> Thank you.
>> Kind Regards,
>> Eirini
>> Eirini Mantesi
>> Research Engineer
>> School of Civil and Building Engineering
>> Loughborough University
>> T: +447462665904
>> E: <mailto:E.Mantesi at lboro.ac.uk>E.Mantesi at lboro.ac.uk
>> <mailto:E.Mantesi at lboro.ac.uk>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> <mailto:TRNSYS-users at lists.onebuilding.org>
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>>
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> <mailto:TRNSYS-users at lists.onebuilding.org>
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com <http://www.tess-inc.com/>
> http://www.trnsys.com <http://www.trnsys.com/>
>
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160307/769f6a41/attachment-0003.htm>
More information about the TRNSYS-users
mailing list