[TRNSYS-users] New heating / cooling type
    David BRADLEY via TRNSYS-users 
    trnsys-users at lists.onebuilding.org
       
    Fri Jul 15 08:02:16 PDT 2016
    
    
  
Issmail
   Type56 has built-in idealized heating and cooling types that will 
meet a setpoint temperature if you have set them up to have unlimited 
heating and cooling capacity. What you are looking at in TRNBuild is the 
heating set point temperature that is being met. The temperature 
maintained in the room is based on the equation 5*schedule + 15 where 
schedule is the value of a SCHEDULE function defined in the TRNBuild 
schedule manager. It probably has a value of either 0 or 1 depending on 
when the building is occupied. This would mean that when the building is 
unoccupied the heating set temperature would be 15C and that when the 
building is occupied, the heating set temperature would be 20C.
kind regards,
  David
On 07/14/2016 08:42, Issmail Ouhallou via TRNSYS-users wrote:
> Dear users,
>   In the order of setting a new heating type, I don't understand the 
> difference between the */room temperature control/* when it's set up 
> to constant value (20 °C for instance) and the schedule value 
> (5*schedule + 15 °C for instance) !!
>   Can some one explain to me the difference, specially for the second 
> value : 5*schedule + 15 °C ?
>
> Best regards,
> ISSMAIL.
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160715/5c6bcc73/attachment-0002.htm>
    
    
More information about the TRNSYS-users
mailing list