[TRNSYS-users] Convergence limits at hot temperatures
hotline via TRNSYS-users
trnsys-users at lists.onebuilding.org
Tue Aug 30 06:22:38 PDT 2016
Dear Camille,
are you using TRNFlow or do your ventilation or infiltration rates depend on dT between inside and outside?
This could lead to very high air change rates when reaching Tzone=70°C and those high air change rates could lead to iteration problems.
Best
Jakob
_________________________________________________________________________________________________
Jakob Merk
TRNSYS Software Team
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax: +49 711 67976-11
Email: hotline at transsolar.com<mailto:hotline at transsolar.com>
Web: www.trnsys.de<http://www.trnsys.de/>
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von via TRNSYS-users
Gesendet: 30 August 2016 11:32
An: trnsys-users at lists.onebuilding.org
Betreff: [TRNSYS-users] Convergence limits at hot temperatures
Dear all,
I'm trying to use TRNSYS to simulate a building in summer extreme conditions, up to 45°C outdoor and with high gains, inside temperatures reach 70°C.
I have convergence problems. Is TRNSYS adapted to these temperatures ? What are the limits of the software for inside temperature ?
Best regards,
Camille
ENGIE Mail Disclaimer: http://www.engie.com/disclaimer/disclaimer-fr.html
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160830/c0983d0f/attachment.htm>
More information about the TRNSYS-users
mailing list