[TRNSYS-users] Calling Contam
Dols, William Stuart (Fed)
william.dols at nist.gov
Wed Apr 20 07:20:12 PDT 2016
For the record, this issue was addressed via direct email.
The solution:
Open the Global Infos dialog via the Assembly->Control Cards menu.
Delete ASSIGN statements in the Simulation cards dialog box.
[cid:image001.png at 01D19AEE.39B60860]
Double-click Type98 icon and establish the two external files necessary for the simulation, PRJ and VEF.
[cid:image002.png at 01D19AEE.39B60860]
- Stuart
From: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] On Behalf Of EWA engineering
Sent: Wednesday, April 20, 2016 9:24 AM
To: trnsys-users at lists.onebuilding.org
Subject: [TRNSYS-users] Calling Contam
Dear all,
I try to use Contam with trnsys 17-02-005.
But I always receive the same error :
Fatal Error at time : 0.000000
Generated by Unit : Not applicable or not available
Generated by Type : Not applicable or not available
TRNSYS Message 71 : An ASSIGNED logical unit number is already in use, either by the TRNSYS kernal or by a Type
Reported information : Logical Unit 41
The logical unit 41 is the project file created by Contam. I tried to change the number with 441 but Trnsys report the same error with 441.
I try many times with the procedure described on the Contam website but nothing changes.
Could you please help me ?
Regards,
Frédéric Oleksandrow
www.ewa-engineering.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160420/046e0aa6/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 46624 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160420/046e0aa6/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 34397 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20160420/046e0aa6/attachment-0007.png>
More information about the TRNSYS-users
mailing list