The number of loops is the number of individual pipes that are all
fed from a single manifold. Section 5.2.4.2.3 of the
05-MultizoneBuilding manual covers the "how to define" aspect of active
layers. The flow that you specify is divided evenly between the pipe
loops and that in turn has an effect on the internal heat transfer
coefficient between the pipe wall and the liquid in the pipe. Section
5.4.4 of the same manual covers the mathematics that underlie the active
layer model. If you haven't found enough detail or don't find the
answers you are looking for in those sections, please let your
distributor know!
best,
David
On 09/02/2015 04:26, Anand N wrote:
> Hello,
> I am working on TRNSYS 17 and I have a question regarding the TRNBuild.
>
> What is meant by "Number of loops" in ACTIVE LAYER SPECIFICATIONS tab,
> if under floor heating system is activated. How do we define it?
>
> Please let me know if anyone has an idea about it and how does it
> affect the flow rate. Since nothing is mentioned about this in the
> user -manual, I'm confused about the internal connections in the flooring.
>
> Thanks in advance,
>
> Regards,
> Anand Narasipuram,
> */MSC- ENTECH, KIC InnoEnergy/*,
> Karlsruhe institute of technology
> Karlsruhe, Germany.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150903/146c3c27/attachment-0003.htm>
More information about the TRNSYS-users
mailing list