[TRNSYS-users] Type 108
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Mon Oct 26 13:58:55 PDT 2015
    
    
  
Safwan,
  You will need to define an equation that has a value of 1 during the 
time of year when it is okay for the chiller to run and a 0 at other 
times. The equation might be:
okChiller = AND(GT(TIME,3000),LT(TIME,5000))
   The result of the equation is a 1 whenever the hour of the year is 
between 3000 and 5000. You will obviously have to adjust the times to 
your cooling season. You then multiply the Type108 output by the result 
of the equation before passing it to the chiller.
regards,
  David
On 10/24/2015 08:43, Safwan Kanan wrote:
> Dear All,
>
>  I am using Type 108 to control room temperature and also to control 
> absorption chiller,cooling tower and pumps, that's mean all the system 
> will be (on or off ) together depending on room temperature.
> I want that because I running the simulation for a whole year, so 
> chiller should be off in winter.
>
> Please correct me if I am wrong?
>
> Safwan Kanan
> PhD student
> University of Manchester
> Manchester
> M13 9PL
> UK
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151026/0e405139/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list