The schedules that are built in to TRNBuild are either daily or weekly 
(and repeat automatically). If you want longer schedules you will need 
to specify an INPUT instead of a SCHEDULE in TRNBuild. You can then use 
a standard TRNSYS Type (such as Type14 or some of the schedule types in 
the TESS Applications Library) to define appropriate schedules.
kind regards,
  David
On 5/20/2015 4:29 AM, Dalal Badreddine wrote:
> Hello,
>
> I'm working on a multizone building simulation, and i need to define 
> an annual scenario for the shading. All i can find is a weekly or a 
> daily one.
>
>  Does anyone know how i can do an annual scenario?
>
> Thank you!
>
> -- 
>
> *
> *Badreddine Dalal*
> Elève ingénieur en Génie Civil à l'EHTP
> Etudiante en Master GC à l'Ecole Centrale de Lille
> **
> *
>
> Tél : 00 33 7 52 41 34 23
> *
> E-mail : Badreddinedalal at gmail.com <mailto:Badreddinedalal at gmail.com>
>
>
>
> *
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150520/801bd688/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list