    Jeff Thornton 
    thornton at tess-inc.com
       
    Fri May  1 07:03:22 PDT 2015
    
    
  
Re: Type997
Imagine you have insulation above the horizontal ground heat exchanger on the soil surface that stretches out 4 meters beyond the edges of the pipe area and no insulation beyond that.  This parameter would then be set to 4.
My bigger question is why you would be using a detailed ground heat exchanger model when you only have one pipe.  I would recommend one of the simpler buried pipe models - unless you need one of the unique features of the ground heat exchanger model (surface insulation, multiple ground layers, etc) 
Jeff
Sent from my iPhone
> On May 1, 2015, at 6:12 AM, SANJEEV JAKHAR <sanjeev.jakhar at pilani.bits-pilani.ac.in> wrote:
> 
> Dear sir,
> Within the GHP library, Ground heat exchanger (Type 997), i didnt understand the parameter "12" Length of surface extension: left (The distance that the surface (insulating layer or conditioned space) above the ground heat exchanger pipes extends beyond the edges of the pipes and towards the left (decreasing x)). 
> By default it is taking 2 m length. How does the change in this parameter effects the performance if i have taken a system of one pipe in one pipe layer. So please guide me.
> 
> Thanks & Regards,
> 
> Sanjeev Jakhar
> Research Scholar
> Center for Renewable Energy and Environment Development (CREED)
> Mechanical Engineering Department
> Birla Institute of Technology & Science, Pilani 
> Rajasthan - 333031
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150501/b030f667/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list