[TRNSYS-users] About Type-952 for geothermal cooling
    Jeff Thornton 
    thornton at tess-inc.com
       
    Fri May  1 06:57:27 PDT 2015
    
    
  
Re: Type 952 - You can't have a zero thermal conductivity.  An error message in the resulting list file should have pointed that out.  Do you check the list file when you have problems?  That's the VERY first place to start.
To simulate a pipe without insulation, simply set the insulation material properties to something reasonable and set the thickness to zero.
If the model had refused to allow a thickness of zero (this is true of some models) you could have specified a material with a HIGH thermal conductivity and the smallest thickness allowed in order to minimize the resistance to heat transfer of the insulation.
Jeff
Sent from my iPhone
> On May 1, 2015, at 6:29 AM, SANJEEV JAKHAR <sanjeev.jakhar at pilani.bits-pilani.ac.in> wrote:
> 
> Dear Mr. Jeff,
> First of all thank you for your reply I have checked the Type 952 as per your suggestion. However for zero insulation thickness and with zero thermal conductivity it is not working at all.  For zero thickness means there is no thermal conductivity of the insulating material. But when I put default value of thermal conductivity with zero thickness it works. 
> 
> Thanks & Regards,
> 
> Sanjeev Jakhar
> Research Scholar
> Center for Renewable Energy and Environment Development (CREED)
> Mechanical Engineering Department
> Birla Institute of Technology & Science, Pilani 
> Rajasthan - 333031
> 
>> On Wed, Apr 29, 2015 at 7:02 AM, Jeff Thornton <thornton at tess-inc.com> wrote:
>> Dear Sir,
>> 
>> I just dragged out a Type 952 from the GHP Library, set the insulation thickness to zero and it ran just fine - with and without flow.  I checked the source code and there is no mention of a recent bug fix dealing with the insulation thickness.  Are you sure that you don't have som other error causing you problems?
>> 
>> As for the average surface temperature, for most applications it's relatively close to the average air temperature for the site - but not always.  It is also close to the average deep earth temperature for many locations as well.
>> 
>>  
>> 
>> Jeff
>> 
>>  
>> 
>> ---
>> Jeff Thornton
>> President - TESS LLC
>> 22 N. Carroll Street, Madison WI USA 53703
>> Office: (608) 274-2577  Fax: (608) 278-1475
>> www.tess-inc.com
>> E-Mail: thornton at tess-inc.com
>>> On 04/27/2015 1:05 am, SANJEEV JAKHAR wrote:
>>> 
>>> Dear sir/madam,
>>> 
>>> I have a doubt on Type-952 (Buried horizontal pipes) for geothermal cooling in which the system supposed to be buried inside the soil. In the parameters how to define the thickness of insulation since I don't want to give thermal insulation to allow heat transfer between the pipe and soil. If I gave insulation as zero value it is showing some error and simulation no running. Please guide me how to solve the problem.
>>> Also please clarify what is average surface temperature. Is it equivalent to average annual ambient temperature or temperature of soil at a certain depth.
>>> 
>>> Thanks & Regards,
>>>  
>>> Sanjeev Jakhar
>>> Research Scholar
>>> Center for Renewable Energy and Environment Development (CREED)
>>> Mechanical Engineering Department
>>>  
>>> Birla Institute of Technology & Science, Pilani 
>>> Rajasthan - 333031
>>> 
>>> _______________________________________________
>>> TRNSYS-users mailing list
>>> TRNSYS-users at lists.onebuilding.org
>>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>> 
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150501/1365e7b6/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list