[TRNSYS-users] (no subject)

David BRADLEY d.bradley at tess-inc.com
Wed May 20 06:53:38 PDT 2015


The schedules that are built in to TRNBuild are either daily or weekly 
(and repeat automatically). If you want longer schedules you will need 
to specify an INPUT instead of a SCHEDULE in TRNBuild. You can then use 
a standard TRNSYS Type (such as Type14 or some of the schedule types in 
the TESS Applications Library) to define appropriate schedules.
kind regards,
  David


On 5/20/2015 4:29 AM, Dalal Badreddine wrote:
> Hello,
>
> I'm working on a multizone building simulation, and i need to define 
> an annual scenario for the shading. All i can find is a weekly or a 
> daily one.
>
>  Does anyone know how i can do an annual scenario?
>
> Thank you!
>
> -- 
>
> *
> *Badreddine Dalal*
> Elève ingénieur en Génie Civil à l'EHTP
> Etudiante en Master GC à l'Ecole Centrale de Lille
> **
> *
>
> Tél : 00 33 7 52 41 34 23​
> *
> E-mail : Badreddinedalal at gmail.com <mailto:Badreddinedalal at gmail.com>
>
>
>
> *
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150520/801bd688/attachment.htm>


More information about the TRNSYS-users mailing list