[TRNSYS-users] Various configuration in Type-997
Jeff Thornton
thornton at tess-inc.com
Wed May 6 10:38:14 PDT 2015
Re: Type997: The model allows you to tell each pipe where it's inlet
fluid is coming from and the direction of flow. For a serpentine of 5
pipes, you would specify the flow pattern as:
Pipe 1: Inlet=0 (Connected as an input), Direction=1
Pipe 2: Inlet=1 (From Pipe 1), Direction = 2
Pipe 3: Inlet=2 (From Pipe 2), Direction = 1
Pipe 4: Inlet=3 (From Pipe 3), Direction = 2
Pipe 5: Inlet=4 (From Pipe 4), Direction = 1
Jeff
---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton at tess-inc.com
On 05/06/2015 10:39 am, SANJEEV JAKHAR wrote:
> Dear sir, In Type 997 it is mention that it can be used for various configuration like serpentine double serpentine etc. I have simulated the model for single pipe. I would like to know how to proceed for serpentine and double serpentine cases. Do I have to change in any parameter to make serpentine case.
> Thanks & Regards,
>
> Thanks & Regards,
>
> SANJEEV JAKHAR
> Research Scholar
> Center for Renewable Energy and Environment Development (CREED)
> Mechanical Engineering Department
>
> BIRLA INSTITUTE OF TECHNOLOGY & SCIENCE, PILANI
> Rajasthan - 333031
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org [1]
Links:
------
[1]
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150506/fb62ca5a/attachment.htm>
More information about the TRNSYS-users
mailing list