[TRNSYS-users] end of file error
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Tue Jun  9 12:37:51 PDT 2015
    
    
  
Suhrid,
   Type15 rewinds the data file as soon as it gets to the end so it 
/shouldn't/ get an "end of file" error unless the file is blank. I'm 
guessing it might be best to send your project to your distributor's 
hotline though since it sounds as though you are getting an end of file 
error when you shouldn't be.
regards,
  David
On 06/09/2015 13:36, Suhrid A Deshmukh wrote:
> Thanks for the prompt response!
> What do you fix if the end of file is happening in type 15-2? It tries 
> to read the weather files in the TMY2 format and some of them it reads 
> fine and some of them it doesnt.
>
> Regards,
> Suhrid
> ------------------------------------------------------------------------
> *From:* David BRADLEY [d.bradley at tess-inc.com]
> *Sent:* Tuesday, June 09, 2015 1:22 PM
> *To:* TRNSYS users mailing list at OneBuilding.org; Suhrid A Deshmukh
> *Subject:* Re: [TRNSYS-users] end of file error
>
> Suhrid,
>  Check to make sure that the 10th parameter of Type51 sets the correct 
> number of data points that are in your external file. The default 
> value of the 10th parameter is 24. If your data file has less than 24 
> points in it then you'll need to modify the value of that parameter 
> accordingly.
> regards,
>  David
>
>
> On 6/8/2015 10:33 PM, Suhrid A Deshmukh wrote:
>> Hello all,
>> I am trying to simulate a cooling tower Type 51 with an external file 
>> and the end of file is reached before the simulation ends. Does 
>> anyone know the fix to this?
>>
>> Regards,
>> Suhrid
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI  53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com
>
> http://www.tess-inc.com
> http://www.trnsys.com
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150609/4c5d57c1/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list