[TRNSYS-users] end of file error

Suhrid A Deshmukh suhrid at mit.edu
Wed Jun 10 15:22:16 PDT 2015


Hello David,

I am trying to include a chiller component into my TRNSYS model. Get an error that says the Chiller might be operating outside the acceptable range. Is this range the range of the cooling loads, the temperatures etc? What exactly is it?

Regards,
Suhrid
________________________________
From: David BRADLEY [d.bradley at tess-inc.com]
Sent: Tuesday, June 09, 2015 3:37 PM
To: Suhrid A Deshmukh; TRNSYS users mailing list at OneBuilding.org
Subject: Re: [TRNSYS-users] end of file error

Suhrid,
  Type15 rewinds the data file as soon as it gets to the end so it shouldn't get an "end of file" error unless the file is blank. I'm guessing it might be best to send your project to your distributor's hotline though since it sounds as though you are getting an end of file error when you shouldn't be.
regards,
 David


On 06/09/2015 13:36, Suhrid A Deshmukh wrote:
Thanks for the prompt response!
What do you fix if the end of file is happening in type 15-2? It tries to read the weather files in the TMY2 format and some of them it reads fine and some of them it doesnt.

Regards,
Suhrid
________________________________
From: David BRADLEY [d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>]
Sent: Tuesday, June 09, 2015 1:22 PM
To: TRNSYS users mailing list at OneBuilding.org; Suhrid A Deshmukh
Subject: Re: [TRNSYS-users] end of file error

Suhrid,
 Check to make sure that the 10th parameter of Type51 sets the correct number of data points that are in your external file. The default value of the 10th parameter is 24. If your data file has less than 24 points in it then you'll need to modify the value of that parameter accordingly.
regards,
 David


On 6/8/2015 10:33 PM, Suhrid A Deshmukh wrote:
Hello all,
I am trying to simulate a cooling tower Type 51 with an external file and the end of file is reached before the simulation ends. Does anyone know the fix to this?

Regards,
Suhrid



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org



--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>

http://www.tess-inc.com
http://www.trnsys.com


--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>

http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150610/970918b2/attachment.htm>


More information about the TRNSYS-users mailing list