[TRNSYS-users] Determining TrnBuild Boundary temperatures in boundary type.
Marion Hiller
Hiller at Transsolar.com
Fri Jul 3 00:14:33 PDT 2015
Muhammad and Tim,
in fact it is a little different:
Boundary identical
- the back surface receives the same gains as the front side surface
- the starnode temperature of the back side is the starnode temperature of the front side
- the used heat transfer coefficient
If the construction is symmetrical and the heat transfer coefficients (htc) are the same then
the back surface temperature = front surface temperature.
If the construction isn’t symmetrical and/or different htc are defined the temperatures are different.
Boundary userdefined
- The user defines a temperature which is coupled to the back surface temperature by the
defined htc to the back surface temperature.
If you want to set a defined back surface temperature there is an option to define “direct contact”
by setting htc = 0.0001. I know that it is strange to defined a very low HTC for obtaining perfect coupling,
But that’s the way it is defined in the code.
Marion
-----------------------------------------------------------------------------------------------------------------------------------------------------------
Dipl.-Ing. Marion Hiller
TRANSSOLAR Energietechnik GmbH
Stuttgart - Munich - New York - Paris
t: +49.711.67976.0<tel:%2B49.711.67976.27> f: +49.711.67976.11<tel:%2B49.711.67976.11>
www.transsolar.com/<http://www.transsolar.com/>
KlimaEngineering - Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347 / Steuernummer: 99073/00911 / USt-IdNr.: DE 152272639
Geschäftsführer: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von mcdowell at tess-inc.com
Gesendet: Donnerstag, 2. Juli 2015 22:59
An: TRNSYS users mailing list at OneBuilding.org
Betreff: Re: [TRNSYS-users] Determining TrnBuild Boundary temperatures in boundary type.
Muhammad Talha -
Identical means that the back surface temperature is the same as the front surface temperature.
Userdefined means that the back surface temperature will be set by the user, either as a constant or as an input.
Regards,
Tim
---
Timothy P. McDowell
Executive Vice President
Thermal Energy System Specialists, LLC
22 N Carroll St, Suite 370
Madison, WI 53703
608-274-2577
On 2015-07-02 15:30, Muhammad Talha wrote:
Dear TRNSYS users,
Is there a way to determine the boundary temperature in the boundary type in TrnBuild. I am using the boundary as category for floor but can't comprehend what identical means. I want to determine heat loss through the floor of my building.
Mohammad Talha
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150703/de90c4f8/attachment-0003.htm>
More information about the TRNSYS-users
mailing list