Meer,
in Energy Rage Control Type56 is computing the zone loads on the HVAC
system. If you want a /very/ rough idea of the energy use of the
building you can simply multiply those loads by an average COP or
efficiency. A better method is to impose those loads on a model of the
HVAC system either by selecting energy rate control HVAC system
components that take load as an input (there are relatively few of
these) or by imposing the load on the water or air loop in the building
using Type682 or Type693 in the TESS Loads and Structures library.
kind regards,
David