Safwan,
   I'd recommend you read the 04-MathematicalReference.pdf entry 
concerning Type108 if you are confused and have not already done so. 
Type108 is a very simple on/off controller with hysteresis. A cooling 
signal will turn on if the monitored temperature rises above the cooling 
set point plus half the deadband temperature difference. The signal will 
turn off if the monitored temperature falls to the cooling setpoint 
minus half the deadband.
regards,
  David


On 2/8/2015 15:16, Safwan Kanan wrote:
> Dear All,
>
> I am quite confused about using Type 108 for control building, pumps, 
> chiller and fan, I want to know what are the best values or ranges for 
> monitoring temperature, 1st stage cooling set point and temperature 
> dead band. I tried different values and I got different results. So 
> could you advice me in this issue.
>
> I am looking to hearing from you soon.
>
> Safwan Kanan
> Manchester University
> M13 9PL
> UK
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150209/37910961/attachment-0002.htm>


More information about the TRNSYS-users mailing list