[TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
Vinod
vviinnoodd at rediffmail.com
Fri Dec 18 04:32:31 PST 2015
David Sir,
Thank you very much for your positive and prompt response. I need some more clarifications in this regard.
I've a collector whose hot water drain should be started only if outlet temperature is above 50 degree Celsius by switching ON the pump.
Kindly guide me on connections as per attached image.
Thanks a lot.
Regards
VeekayIndia
From: David BRADLEY <d.bradley at tess-inc.com>
Sent: Thu, 17 Dec 2015 03:05:05
To: "TRNSYS users mailing list at OneBuilding.org" <trnsys-users at lists.onebuilding.org>, vviinnoodd at rediffmail.com
Subject: Re: [TRNSYS-users] HELP: In TRNSYS 17: How to connect a thermostat switch (Type 2b) to switch ON a pump at a particular temperature range else keep the pump OFF.
Veekay,
There are two ways that Type2 can be used. Most commonly it is
used as a differential controller such that it turns on when the
difference between two temperatures exceeds a certain amount and
then stays on until the difference between those temperatures falls
to a different amount. You'd use this in a solar thermal system when
you want to turn on the collector if the collector temperature
exceeds the storage tank temperature by (for example) 10C no matter
what the temperature of the storage tank. This was the method that
Alastair correctly suggested.
You can also use Type2 like a more traditional thermostat in which
case you typically want to turn on a device when a monitored
temperature exceeds (or falls below) a certain set point value.
There are proformas for Type2 set up to do this. They are located in
Controllers: Aquastat: Heating Mode and Controllers: Aquastat:
Cooling Mode. Alternatively you can use Type108 which, while it
allows for more than one stage of control, can also be used as a
simple thermostat in either heating or cooling mode.
kind regards,
David
On 12/16/2015 12:44, Vinod wrote:
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151218/8cef7ebd/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Type2b_connection_help.jpg
Type: image/jpeg
Size: 59713 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20151218/8cef7ebd/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list