[TRNSYS-users] Solar Thermal Collector outlet temperature

Jeff Thornton thornton at tess-inc.com
Fri Aug 21 08:28:56 PDT 2015


Arnoud,

Are you also changing the area parameter?  That parameter is the total array area - not the module area.  Also pay attention to the flow rate - as that is also the array flow rate.

Otherwise, no, you should get the same temperature.  Imagine a single 4 x 8 collector, keeping the same size, flow rate etc, wouldn't you expect eight 4 x 1 collectors in series to produce the same result?

Jeff Thornton
TESS

Sent from my iPhone

> On Aug 21, 2015, at 3:45 AM, Arnaud Candaele <arnaud.candaele at gmail.com> wrote:
> 
> Hi,
> 
> I'm trying to model a simple solar thermal collector, using Type1a.
> 
> I created a very simple test case, basically just taking the outdoor temperature and solar radiation, and plotting the outlet temperature.
> The thing is, I'm changing the number of collectors in series, and the plotted outlet temperature doesn't change at all.
> Isn't it supposed to change ?
> 
> Thanks for any help !
> 
> Arnaud