[TRNSYS-users] Air layer in Trnbuild
David BRADLEY
d.bradley at tess-inc.com
Thu Apr 30 07:45:50 PDT 2015
Marko,
The reason that the "airlayer" material in the TRNBuild libraries is
massless and has no thickness is that narrow air gaps (i.e. airgaps with
little or no convection in them) can be assumed to provide thermal
resistance in the wall. When you have a wide air gap then the convection
within that airgap becomes important and you cannot correctly account
for it as though it were part of the wall. What I would recommend you do
is to treat that 70cm air gap as though it were one or more airnodes
separated from the ambient and the conditioned space by "walls" that
consist only of your polyester foil (treated as massless layers offering
only a thermal resistance). You can set the convection coefficients on
the inside of those two layers as computed internally by Type56. This is
probably still not an ideal treatment of the situation either but in my
opinion it is more correct than lumping the air gap into the wall.
kind regards,
David
On 4/29/2015 1:58 PM, Marko Mancic wrote:
> Hi Trnsys users,
>
> I am trying to create a model of a lightweight contruction sport hall,
> which consists of two leyers of special Polyester foils, and a 70cm
> air layer between. In reality, the construction is streched and held
> in place by a wood sceleton.
>
> I have noticed, that whichever air layer is chosen from the library,
> it is modelled as massless, and the tickness is 0.
>
> How can I change the tickness of the Air layer?
>
> In addition, I get the following error messages when I try to save the
> project "error when trying to create wall transfer coefficients"
> " unable to find root, after indication that root exists"
> "Maybe time base is to small"
>
> What could be the couse of the error I am getting?
>
>
> Thank you for helping!
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150430/acc75fad/attachment-0003.htm>
More information about the TRNSYS-users
mailing list