[TRNSYS-users] Cooling load or total heat transfer rate
David BRADLEY
d.bradley at tess-inc.com
Mon Apr 13 12:46:43 PDT 2015
Safwan,
There is a very important difference between a building cooling load
and the total heat transfer rate being computed by Type697. A building
total cooling load is the amount of energy (sensible and latent) that
must be removed from a space in order to maintain a setpoint. Type697 is
reporting the amount of energy that it actually removed from the air
stream. If Type697 isn't maintaining the setpoints that you want it to
then the amount of energy that it is removing from the space and the
building's cooling load are not going to be equivalent.
I would recommend that you go through the tutorial called "Temperature
Level Control from Energy Rate Control" that can be downloaded from:
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm.
The tutorial should answer your questions about the how to obtain the
loads or the energy transferred by the system.
regards,
David
On 4/6/2015 9:41 PM, Safwan Kanan wrote:
> Dear All,
>
> I am simulating solar cooling system, shall I depend on total heat
> transfer rate output from Type 697( cooling coil) as a cooling load
> for building or not? If not shall I need to calculate the cooling load
> for building by Trnsys? if yes ,could you please explain HOW in
> details? I used Type 56.
>
> I am looking forward to hearing from you.
> Regards,
>
> Safwan Kanan
> The University of Manchester
> Manchester
> M13 9PL
> UK
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150413/8e5dec55/attachment-0003.htm>
More information about the TRNSYS-users
mailing list