Thank you for your answer Angel,
1) Yes but I have an heating district system with more than one component
(boilers, tanks, absorption chiller for summer operation, ...) I don't know
if I have to change the type of heat exchangers linked to the buildings
(for summer operation)...
2) I don't know how to model a control system... I have to change the
operation from winter to summer and the opposite. Could you help me?
Thank you again for your availability,
Kind Regards,
Laura
2015-04-01 15:18 GMT+02:00 <trnsys-users-request at lists.onebuilding.org>:
> Send TRNSYS-users mailing list submissions to
>         trnsys-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
> or, via email, send a message with subject or body 'help' to
>         trnsys-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
>         trnsys-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
>    1. Re: Help to Heating District with Trnsys16.1 model
>       (Laura Fasciolo)
>    2. Re: Help to Heating District with Trnsys16.1 model (Angel Carrera)
>    3. Information Type 941 (Melanie Monecke)
>
>
> ---------- Messaggio inoltrato ----------
> From: Laura Fasciolo <lally.fasciolo at gmail.com>
> To: David BRADLEY <d.bradley at tess-inc.com>,
> trnsys-users at lists.onebuilding.org,
> trnsys-users-request at lists.onebuilding.org
> Cc:
> Date: Wed, 1 Apr 2015 11:49:47 +0200
> Subject: Re: [TRNSYS-users] Help to Heating District with Trnsys16.1 model
> Thank you so much David for your answer!
>
> I have another 2 questions:
>
> 1) In the case of summer operation, I have to "exchange the cold", so I
> have to use a cold heat exchanger that, powered by a cold fluid, must cool
> the another fluid. Which kind of heat exchanger I have to use? Which type
> do you suggest me?
>
> 2) I have to simulate both the winter operation and the summer operation.
> Is there a way to change the conditions of the system with its parameters
> during the same simulation?
>
> Thank you again!
> Kind regards,
> Laura
>
>
>
> 2015-03-25 19:07 GMT+01:00 David BRADLEY <d.bradley at tess-inc.com>:
>
>>  Laura,
>>  Type907 in the TESS CHP library has the features that you are looking
>> for.
>> kind regards,
>>  David
>>
>>
>>
>> On 3/23/2015 4:55 PM, Laura Fasciolo wrote:
>>
>> Thank you so much David for your answer!
>>
>> I need a cogenerator, an engine which has a hot water flowrate and a
>> certain temperature, as outputs. This is the reason why I asked for help
>> with an ICE component and an heat generator.
>>
>> Could you help me? Can I find a type for a cogenerator, an engine which
>> has a hot water flowrate and a certain temperature, as outputs? I have
>> Trnsys 16.1 with TESS library.
>>
>>  Thank you again!
>>
>>  Best Regards,
>> Lally
>>
>>
>>
>> 2015-03-23 21:53 GMT+01:00 David BRADLEY <d.bradley at tess-inc.com>:
>>
>>>  Lally,
>>>  There is a diesel engine generator component available in the standard
>>> TRNSYS library (Type120). There is a different model of an internal
>>> combustion engine in the TESS CHP library (which is an add-on to the
>>> standard package). I am not sure what (specifically) you mean by a heat
>>> generator. There are quite a few TRNSYS components that simulate devices
>>> that generate heat.
>>> kind regards,
>>>  David
>>>
>>>
>>> On 3/23/2015 9:05 AM, Laura Fasciolo wrote:
>>>
>>> Hi Trnsys people! I'm trying to simulate a model of Heating District
>>> with Trnsys 16.1 , in my final thesis at the university. Does somebody know
>>> some Trnsys Types to simulate an ICE component and a Heat Generator?
>>> Thanks to everybody!
>>>
>>>
>>>  _______________________________________________
>>> TRNSYS-users mailing listTRNSYS-users at lists.onebuilding.orghttp://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>>
>>>
>>> --
>>> ***************************
>>> David BRADLEY
>>> Principal
>>> Thermal Energy Systems Specialists, LLC
>>> 22 North Carroll Street - suite 370
>>> Madison, WI  53703 USA
>>>
>>> P:+1.608.274.2577
>>> F:+1.608.278.1475d.bradley at tess-inc.com
>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>
>>>
>>
>> --
>> ***************************
>> David BRADLEY
>> Principal
>> Thermal Energy Systems Specialists, LLC
>> 22 North Carroll Street - suite 370
>> Madison, WI  53703 USA
>>
>> P:+1.608.274.2577
>> F:+1.608.278.1475d.bradley at tess-inc.com
>> http://www.tess-inc.comhttp://www.trnsys.com
>>
>>
>
>
> ---------- Messaggio inoltrato ----------
> From: Angel Carrera <angel.carrera at aiguasol.coop>
> To: "TRNSYS users mailing list at OneBuilding. org" <
> trnsys-users at lists.onebuilding.org>
> Cc:
> Date: Wed, 1 Apr 2015 12:26:19 +0200
> Subject: Re: [TRNSYS-users] Help to Heating District with Trnsys16.1 model
>
>
> Dear Laura,
>
> Heat exchangers in trnsys can work both for heating and cooling, you don't
> have to change the component due to this. Depending on the component you
> choose, in psrticular if the hx properties are inputs or parameters, you
> will end up with different hydtaulic layouts in your model: you can have
> two hx with mixers and diverters on the network side, or just one hx with
> the mixers and div on the generator side. I recommend you type 5 or type 91.
> About changing the conditions, depends on what vonditions, but remember
> that parameters cannot be chaged during a simulation, regsrds
>
> Angel
> El 01/04/2015 11:49, "Laura Fasciolo" <lally.fasciolo at gmail.com> escribió:
>
>> Thank you so much David for your answer!
>>
>> I have another 2 questions:
>>
>> 1) In the case of summer operation, I have to "exchange the cold", so I
>> have to use a cold heat exchanger that, powered by a cold fluid, must cool
>> the another fluid. Which kind of heat exchanger I have to use? Which type
>> do you suggest me?
>>
>> 2) I have to simulate both the winter operation and the summer
>> operation. Is there a way to change the conditions of the system with its
>> parameters during the same simulation?
>>
>> Thank you again!
>> Kind regards,
>> Laura
>>
>>
>>
>> 2015-03-25 19:07 GMT+01:00 David BRADLEY <d.bradley at tess-inc.com>:
>>
>>>  Laura,
>>>  Type907 in the TESS CHP library has the features that you are looking
>>> for.
>>> kind regards,
>>>  David
>>>
>>>
>>>
>>> On 3/23/2015 4:55 PM, Laura Fasciolo wrote:
>>>
>>> Thank you so much David for your answer!
>>>
>>> I need a cogenerator, an engine which has a hot water flowrate and a
>>> certain temperature, as outputs. This is the reason why I asked for help
>>> with an ICE component and an heat generator.
>>>
>>> Could you help me? Can I find a type for a cogenerator, an engine which
>>> has a hot water flowrate and a certain temperature, as outputs? I have
>>> Trnsys 16.1 with TESS library.
>>>
>>>  Thank you again!
>>>
>>>  Best Regards,
>>> Lally
>>>
>>>
>>>
>>> 2015-03-23 21:53 GMT+01:00 David BRADLEY <d.bradley at tess-inc.com>:
>>>
>>>>  Lally,
>>>>  There is a diesel engine generator component available in the standard
>>>> TRNSYS library (Type120). There is a different model of an internal
>>>> combustion engine in the TESS CHP library (which is an add-on to the
>>>> standard package). I am not sure what (specifically) you mean by a heat
>>>> generator. There are quite a few TRNSYS components that simulate devices
>>>> that generate heat.
>>>> kind regards,
>>>>  David
>>>>
>>>>
>>>> On 3/23/2015 9:05 AM, Laura Fasciolo wrote:
>>>>
>>>> Hi Trnsys people! I'm trying to simulate a model of Heating District
>>>> with Trnsys 16.1 , in my final thesis at the university. Does somebody know
>>>> some Trnsys Types to simulate an ICE component and a Heat Generator?
>>>> Thanks to everybody!
>>>>
>>>>
>>>>  _______________________________________________
>>>> TRNSYS-users mailing listTRNSYS-users at lists.onebuilding.orghttp://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>>>
>>>>
>>>> --
>>>> ***************************
>>>> David BRADLEY
>>>> Principal
>>>> Thermal Energy Systems Specialists, LLC
>>>> 22 North Carroll Street - suite 370
>>>> Madison, WI  53703 USA
>>>>
>>>> P:+1.608.274.2577
>>>> F:+1.608.278.1475d.bradley at tess-inc.com
>>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>>
>>>>
>>>
>>> --
>>> ***************************
>>> David BRADLEY
>>> Principal
>>> Thermal Energy Systems Specialists, LLC
>>> 22 North Carroll Street - suite 370
>>> Madison, WI  53703 USA
>>>
>>> P:+1.608.274.2577
>>> F:+1.608.278.1475d.bradley at tess-inc.com
>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>
>>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at lists.onebuilding.org
>> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>>
>>
>
> ---------- Messaggio inoltrato ----------
> From: Melanie Monecke <21mome1bke at hft-stuttgart.de>
> To: "." <trnsys-users at lists.onebuilding.org>
> Cc:
> Date: Tue, 31 Mar 2015 15:38:58 +0200 (CEST)
> Subject: [TRNSYS-users] Information Type 941
> Dear Sirs,
>
> Could you please send me a documentation with informations about Type 941.
> Thank you very much!
>
> Yours sincerely,
>
>
> Melanie Monecke
>
>
> KlimaEngineering
> Hochschule für Technik
> Schellingstraße 24
> 70174 Stuttgart
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20150401/405d0744/attachment-0003.htm>
    
    
More information about the TRNSYS-users
mailing list