Hi Pauline,
I look at your project and see in your b17 file that surfaces 27 (Zone1)
and 97 (Zone7) have the same area as the wall in which they are defined.
Maybe you can reduce the window area (for example 8.9 m² in a wall of 9
m²), or define your window without wall. For doing that, select
additionnal window in Trnbuild and add a window without wall (just as
shown here below)
After correcting that, the project seems to work fine.
One other remark : Type34 works with isotropic sky model. You may change
the 3rd parameter of type15 to"1" instead of "5".
Hope this helps
Best regards
--
Logo_ITF
*Adrien JEZEQUEL*
Simulation Dynamique - Calculs numériques
62 rue du Bolliet
73230 SAINT-ALBAN-LEYSSE
Tél : +33(0) 479 750 029
Fax : +33(0) 479 852 122
a.jezequel at itf.biz <mailto:a.jezequel at itz.biz>
www.itf.biz <http://www.itf.biz>
Feuille
Le 06/10/2014 08:53, Pauline GELIN a écrit :
>
> Marion,
>
> Thanks a lot for your proposal.
>
> Please find attached the different files of my project.
>
> I thank you very much in advance for any help you could give me.
>
> Best Regards,
>
> *Cordialement,*
>
> **
>
> *Pauline GELIN*
>
> *Ingénieur Conception environnementale*
>
> **
>
> cid:image001.jpg at 01CFAA73.752A6F70
>
> **
>
> cid:image006.jpg at 01CE062A.F4C2C000
>
> 10 avenue des canuts
>
> 69120 VAULX EN VELIN
>
> T : 04.37.45.33.33
>
> *Ligne directe : 04.37.45.33.47*
>
> **
>
> *www.katene.coop***
>
> *www.quadriplus-groupe.com* <http://www.quadriplus-groupe.com/>**
>
> *www.woopa.coop* <http://www.woopa.coop/>**
>
> *De :*TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org]
> *De la part de* Marion Hiller
> *Envoyé :* lundi 6 octobre 2014 08:43
> *À :* 'TRNSYS users mailing list at OneBuilding.org'
> *Objet :* Re: [TRNSYS-users] Problem of pane temperature divergence
>
> Pauline,
>
> it is hard to tell without looking at your project.
>
> If you send the project, I can have a look at it.
>
> Marion
>
> *Von:*TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org]
> *Im Auftrag von *Pauline GELIN
> *Gesendet:* Donnerstag, 2. Oktober 2014 17:02
> *An:* TRNSYS users mailing list at OneBuilding.org
> (trnsys-users at lists.onebuilding.org
> <mailto:trnsys-users at lists.onebuilding.org>); trnsys-users
> (trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>)
> *Betreff:* [TRNSYS-users] Problem of pane temperature divergence
>
> Hi,
>
> like manyusers I have a problem of divergent temperatures for all my
> windows (see message below) with a simple TRNBUILD project, with
> constant CHTC always used in my previous studies, with 2 types 93 for
> gain calculations (I think no link with my problem).
>
> I tried all proposals from mailing list in TRNSYS mailing list archive
> without success.
>
> Does anyone have an idea?
>
> Thank you very in advance for any help.
>
> Best Regards,
>
> *Cordialement,*
>
> **
>
> *Pauline GELIN*
>
> *Ingénieur Conception environnementale*
>
> **
>
> cid:image001.jpg at 01CFAA73.752A6F70
>
> **
>
> cid:image006.jpg at 01CE062A.F4C2C000
>
> 10 avenue des canuts
>
> 69120 VAULX EN VELIN
>
> T : 04.37.45.33.33
>
> *Ligne directe : 04.37.45.33.47*
>
> **
>
> *www.katene.coop***
>
> *www.quadriplus-groupe.com* <http://www.quadriplus-groupe.com/>**
>
> *www.woopa.coop* <http://www.woopa.coop/>**
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cihjhfaj.png
Type: image/png
Size: 35879 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: itf_logo_web.png
Type: image/png
Size: 4327 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: feuille.png
Type: image/png
Size: 3404 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1832 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1058 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 4794 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1835 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/5ef60c72/attachment-0005.jpeg>
More information about the TRNSYS-users
mailing list