[TRNSYS-users] Error
ITF - Adrien JEZEQUEL
a.jezequel at itf.biz
Tue Sep 9 07:39:11 PDT 2014
Hi meryem,
I think you use an automatic heat transfert calculation for a boundary
or an external wall in trnbuild.
Automatic Heat transferts are only allowed for internal wall.
Change that into 'user defined', and you model will run fine.
Hope this helps.
Best regards
Logo_ITF
*Adrien JEZEQUEL*
Simulation Dynamique - Calculs numériques
62 rue du Bolliet
73230 SAINT-ALBAN-LEYSSE
Tél : +33(0) 479 750 029
Fax : +33(0) 479 852 122
a.jezequel at itf.biz <mailto:a.jezequel at itz.biz>
www.itf.biz <http://www.itf.biz>
Feuille
Le 09/09/2014 15:44, meryem serghini a écrit :
>
> /Hello,/
>
> / In my project TRNSYS version 17, when I run the calculation, I get
> an error that I cannot fix:/
>
> /******Fatal Error at time: 0.000000 Generated by Unit: 56Generated by
> Type: 56 Message: Error in automatic calculation for heat transfer
> surface 0 or its adjacent surface!: Automatic heat transfer
> calculation Is Only Allowed on surfaces Within a zone. Please check
> building input file (. bui)!*/
>
> //
>
> /enclosed my project /
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140909/57f3d96b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: itf_logo_web.png
Type: image/png
Size: 4327 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140909/57f3d96b/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: feuille.png
Type: image/png
Size: 3404 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140909/57f3d96b/attachment-0001.png>
More information about the TRNSYS-users
mailing list