[TRNSYS-users] Load definition in Type56

hotline hotline at Transsolar.com
Wed Aug 20 04:17:17 PDT 2014


Juan Francisco,

You're right Q_SENS is part of the energy balance of the zone. As the system boundary of the zone energy balance 
includes the inside surface nodes, all radiative heat fluxes are taken into consideration. 
See p.5-45 in the TRNSYS manual for further explanation.

Best
__________________________________________________________________________________________________

Jochen Lam
TRNSYS Software Team

Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax:        +49 711 67976-11
Email:    jlam at transsolar.com
Web:      www.trnsys.de 


-----Ursprüngliche Nachricht-----
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von JUAN FRANCISCO BELMONTE TOLEDO
Gesendet: Mittwoch, 20. August 2014 12:15
An: TRNSYS users mailing list at OneBuilding.org
Betreff: Re: [TRNSYS-users] Load definition in Type56

I am not sure if I have completely understood this answer. 
Q_sens is not based on an energy balance performed on the zone air?... where is the radiative part there?.

Regards.
Juan Francisco Belmonte

-----Mensaje original-----
De: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] En nombre de hotline Enviado el: miércoles, 20 de agosto de 2014 11:53 a.m.
Para: 'TRNSYS users mailing list at OneBuilding.org'
Asunto: Re: [TRNSYS-users] Load definition in Type56

Yes Q_SENS includes both the radiative and the convective parts.

Best 

__________________________________________________________________________________________________

Jochen Lam
TRNSYS Software Team

Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax:        +49 711 67976-11
Email:    jlam at transsolar.com
Web:      www.trnsys.de 


-----Ursprüngliche Nachricht-----
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von C K Lee
Gesendet: Mittwoch, 20. August 2014 08:05
An: Trnsys discussion group
Betreff: [TRNSYS-users] Load definition in Type56

Dear all.

Can anyone advise if the output QSENS (NType 2) include both convective and radiative loads?  Thank you!

Best Regards
Chun Kwong LEE
City University of Hong Kong

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org



More information about the TRNSYS-users mailing list