[TRNSYS-users] Fw: read weather data type9a
David BRADLEY
d.bradley at tess-inc.com
Wed Aug 13 08:25:15 PDT 2014
Saja,
I would recommend that you start with JUST Type9 and an online
plotter. Use the online plotter to make sure that the data reader is
reading what you think it is reading. It can be tricky to get the data
reader settings correct. For example, you do not want to interpolate
solar radiation readings. You can interpolate temperature and other
readings. There are also a number of parameters that tell whether the
data in the file is given as average values over the data interval or
instantaneous values reported at the end of the interval. Once you are
certain that Type9 is reading the file in a way that makes sense then
look very carefully at the Type16 parameters, especially if your data
file does not start on January 1 at midnight. One of that parameters
asks for the starting /day /of the simulation. Others ask whether the
data being read is in solar time or local (standard) time and if it is
in local time, what the difference in longitude is between the data file
location and the standard longitude for the timezone. These must all be
set correctly in order to avoid the kind of problems that you are seeing.
If you are really stuck after working to get the parameters set
correctly then you should send the project and data file to your
distributor for assistance.
Kind regards,
David
On 8/12/2014 15:55, saja al-rifai wrote:
> hello,
>
> I hope you can answer this question
>
>
>
> I am trying to read my own weather data by using the type9a to import
> global solar radiation and temperature, and using type16c to calculate
> and process the weather data.
>
> The problem that I am trying to plot the outputs of type16c, but
> TRNSYS cannot read the second and third day and 29th day from each
> month. I don't know what the problem, I am sure that the weather data
> exist to all the year,
> I need to read all days to ensure that the weather data available to
> system simulation.
> thanks in advance
> saja
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140813/49c67bf4/attachment-0001.htm>
More information about the TRNSYS-users
mailing list