Type105 is not set up to accommodate a battery in the system. I have
been able to use the Type48 controller in some of my simulations (ones
that did not include electrolyzers and fuel cells) in order to control
the charge and discharge of a battery bank. I have never tried to use
both Type105 and Type48 together. The times when I have had an
electrolyzer, a fuel cell and a battery bank I have always needed to
write my own supervisory controller using a combination of equations and
some new Types that I wrote. The controls of these sorts of stand-alone
power systems are often very specific to the system at hand and so it is
hard to write a generic controller model for them.
Kind regards,
David
On 9/8/2014 08:30, Trans Sys wrote:
> Hello,
>
> from the stand alone power system demo I am (with the help of the
> provided hydrogen executable) I am trying to build a slightly more
> complex system including a battery.
> My question is now the following:
> Can I control the battery (type47 or 185) in the controller type 105?
> Do I have to use any of the type 48?
>
> Thanks a lot in advance
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140908/7368807a/attachment-0002.htm>
More information about the TRNSYS-users
mailing list