[TRNSYS-users] TRNSYS input file (***.air)
Dols, William Stuart
william.dols at nist.gov
Wed Oct 15 13:09:34 PDT 2014
The first number is a laminar flow coefficient.
You can look in the CONTAM documentation for details related to this value.
There is also a LaminarCoef.zip file available in the files section of the Yahoo CONTAM user group that provides the calculation method.
Suffice it to say it is utilized when flows are very low in order to prevent undefined derivatives dF/dP, required for solving the non-linear airflow equations, when pressure difference across flow paths approach zero.
Also, there is a new Type98 that utilizes the full capabilities of the CONTAM simulation engine.
Type98 and associated utilities are available on the NIST CONTAM website.
- Stuart
From: David BRADLEY [mailto:d.bradley at tess-inc.com]
Sent: Wednesday, October 15, 2014 10:01 AM
To: Remon Lapisa; TRNSYS users mailing list at OneBuilding.org
Subject: Re: [TRNSYS-users] TRNSYS input file (***.air)
Remon,
The second number is the flow coefficient and the third number is the flow exponent in the equation that relates the flow through the opening to the pressure difference across the opening. I am not sure what the first value is or how it is computed.
Kind regards,
David
On 10/15/2014 01:06, Remon Lapisa wrote:
Hi everyone,
In the TRNSYS input file of Contam (***.air) we will find some 'flow elements' datas, consisting of 3 values numbers on each line, like the example below (for 5 flow elements):
....
-999 wind pressure profiles:
1 2 5
0 -1 -0.00625 6.94444e-005 0
90 -1 0.00625 6.94444e-005 -5.14403e-007
180 -0.25 0.00625 -6.94444e-005 0
270 -0.25 -0.00625 -6.94444e-005 5.14403e-007
360 -1 0 0 0
...etc
-999 flow elements:
1 0.0321663 0.94 0.5
2 0.090255 1.87 0.5
3 0.25528 3.74 0.5
4 0.723488 7.49 0.5
5 0.0176262 1.08102 0.5
.... etc
In the example above, what values are represented by the 3 bold numbers (0.0176262, 1.08102, 0.5) ??
How to calculate the value of 0.0176262 ?
Thank for the help
remon
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com<mailto:d.bradley at tess-inc.com>
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141015/6b04cb77/attachment-0005.htm>
More information about the TRNSYS-users
mailing list