[TRNSYS-users] Problem of pane temperature divergence
Pauline GELIN
p.gelin at katene.fr
Sun Oct 5 23:53:14 PDT 2014
Marion,
Thanks a lot for your proposal.
Please find attached the different files of my project.
I thank you very much in advance for any help you could give me.
Best Regards,
Cordialement,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image004.jpg at 01CFE142.F7217590]
[cid:image005.jpg at 01CFE142.F7217590]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com/>
www.woopa.coop<http://www.woopa.coop/>
De : TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] De la part de Marion Hiller
Envoyé : lundi 6 octobre 2014 08:43
À : 'TRNSYS users mailing list at OneBuilding.org'
Objet : Re: [TRNSYS-users] Problem of pane temperature divergence
Pauline,
it is hard to tell without looking at your project.
If you send the project, I can have a look at it.
Marion
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] Im Auftrag von Pauline GELIN
Gesendet: Donnerstag, 2. Oktober 2014 17:02
An: TRNSYS users mailing list at OneBuilding.org (trnsys-users at lists.onebuilding.org<mailto:trnsys-users at lists.onebuilding.org>); trnsys-users (trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>)
Betreff: [TRNSYS-users] Problem of pane temperature divergence
Hi,
like many users I have a problem of divergent temperatures for all my windows (see message below) with a simple TRNBUILD project, with constant CHTC always used in my previous studies, with 2 types 93 for gain calculations (I think no link with my problem).
I tried all proposals from mailing list in TRNSYS mailing list archive without success.
Does anyone have an idea?
[cid:image006.png at 01CFE142.F7217590]
Thank you very in advance for any help.
Best Regards,
Cordialement,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image007.jpg at 01CFE142.F7217590]
[cid:image005.jpg at 01CFE142.F7217590]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com/>
www.woopa.coop<http://www.woopa.coop/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1832 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1058 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 4794 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1835 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0017.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: vandoeuvre_001_imported6.tpf
Type: application/octet-stream
Size: 515937 bytes
Desc: vandoeuvre_001_imported6.tpf
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0025.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: vandoeuvre_001.b17
Type: application/octet-stream
Size: 54626 bytes
Desc: vandoeuvre_001.b17
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0026.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: masques_01_new.dat
Type: application/octet-stream
Size: 743 bytes
Desc: masques_01_new.dat
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0027.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: planning_01.dat
Type: application/octet-stream
Size: 485683 bytes
Desc: planning_01.dat
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141006/9fa10597/attachment-0028.obj>
-------------- next part --------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW SAS
WINID=13002 : HINSIDE=16.2 : HOUTSIDE=43.2 : SLOPE=90 : SPACID=1 : WWID=1.8 : WHEIG=2.3 : FFRAME=0.10 : UFRAME=45.00 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW LT
WINID=13002 : HINSIDE=16.2 : HOUTSIDE=43.2 : SLOPE=00 : SPACID=1 : WWID=1.5 : WHEIG=6.0 : FFRAME=0.10 : UFRAME=22.04 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW ALU
WINID=13002 : HINSIDE=16.2 : HOUTSIDE=43.2 : SLOPE=90 : SPACID=1 : WWID=1.5 : WHEIG=2.2 : FFRAME=0.10 : UFRAME= 22.04 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
WINDOW BOIS
WINID=13002 : HINSIDE=16.2 : HOUTSIDE=43.2 : SLOPE=90 : SPACID=1 : WWID=1.5 : WHEIG=2.3 : FFRAME=0.10 : UFRAME= 7.25 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 2.0.167
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: J:\...
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT...
*+++ TITLE=...
*+++ DESCRIPTION=...
*+++ CREATED=...
*+++ ADDRESS=...
*+++ CITY=...
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
-------------- next part --------------
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS15 WINDOW LIB
Desc : Saint Gobain CLIMAPLUS FUTUR AR 1.1 4/15/4
Window ID : 13002
Tilt : 90.0
Glazings : 2
Frame : 11 TRNSYS WIN - 1 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1600.0 mm
Total Width : 1250.0 mm
Glass Height: 1460.3 mm
Glass Width : 1110.3 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 15.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.521 0.524 0.517 0.508 0.495 0.472 0.418 0.312 0.153 0.000 0.439
Abs1 0.022 0.022 0.023 0.023 0.025 0.026 0.027 0.029 0.031 0.000 0.025
Abs2 0.102 0.104 0.112 0.117 0.119 0.123 0.135 0.142 0.105 0.000 0.121
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.355 0.350 0.349 0.352 0.361 0.379 0.420 0.517 0.711 1.000 0.404
Rbsol 0.295 0.289 0.287 0.290 0.299 0.316 0.350 0.430 0.616 0.999 0.337
Tvis 0.782 0.787 0.776 0.763 0.744 0.705 0.618 0.450 0.212 0.000 0.655
Rfvis 0.131 0.124 0.123 0.127 0.142 0.173 0.239 0.388 0.664 1.000 0.214
Rbvis 0.138 0.131 0.128 0.131 0.144 0.169 0.218 0.325 0.551 0.999 0.198
SHGC 0.609 0.613 0.613 0.609 0.598 0.578 0.534 0.435 0.244 0.000 0.544
SC: 0.60
Layer ID# 4054 7202 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.040 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.23 7.55 1.32 1.32 1.05 1.05 1.07 1.07 1.16 1.16
0 6.71 25.47 3.21 7.57 1.39 1.39 1.08 1.08 1.10 1.10 1.20 1.20
783 0.00 12.25 3.28 6.91 1.38 1.38 1.15 1.15 1.13 1.13 1.16 1.16
783 6.71 25.47 3.23 6.66 1.45 1.45 1.20 1.20 1.16 1.16 1.19 1.19
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
13002 Saint Gobain CLIMAPLUS FUTUR AR 1.1 4/15/4 4/15/4 1.1 0.609 0.521 0.355 0.782
_EXTENSION_WINPOOL_END_
_EXTENSION_BuildingGeometry_START_
_EXTENSION_BuildingGeometry_END_
_EXTENSION_ExternalShadingGeometry_START_
_EXTENSION_ExternalShadingGeometry_END_
_EXTENSION_GeoPositionGeometry_START_
_EXTENSION_GeoPositionGeometry_END_
-------------- next part --------------
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER BÉTON_LOUR
CONDUCTIVITY= 7.200 : CAPACITY= 1.00 : DENSITY= 2300
LAYER LVTH38
CONDUCTIVITY= 0.137 : CAPACITY= 1.03 : DENSITY= 16
LAYER PSETH38
CONDUCTIVITY= 0.137 : CAPACITY= 1.45 : DENSITY= 35
LAYER PSETH32
CONDUCTIVITY= 0.115 : CAPACITY= 1.45 : DENSITY= 35
LAYER PUR
CONDUCTIVITY= 0.086 : CAPACITY= 1.45 : DENSITY= 40
LAYER BA13
CONDUCTIVITY= 1.152 : CAPACITY= 1.00 : DENSITY= 900
LAYER LV_FP
CONDUCTIVITY= 0.180 : CAPACITY= 1.03 : DENSITY= 80
LAYER TERRE
CONDUCTIVITY= 3.960 : CAPACITY= 1.00 : DENSITY= 1500
LAYER FLOCAGE
CONDUCTIVITY= 0.148 : CAPACITY= 1.03 : DENSITY= 150
LAYER PSETH30
CONDUCTIVITY= 0.108 : CAPACITY= 1.45 : DENSITY= 30
LAYER CBR
RESISTANCE= 0.550
LAYER AIR
RESISTANCE= 0.044
-------------- next part --------------
WALL MIN1
LAYERS = BÉTON_LOUR
THICKNESS= 0.15
ABS-FRONT= 0.2 : ABS-BACK= 0.2
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 16.2 : HBACK= 16.2
WALL MIN2
LAYERS = BA13 LVTH38 BA13
THICKNESS= 0.013 0.075 0.013
ABS-FRONT= 0.2 : ABS-BACK= 0.2
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 16.2 : HBACK= 16.2
WALL MEE2
LAYERS = BÉTON_LOUR PSETH38
THICKNESS= 0.2 0.18
ABS-FRONT= 0.2 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 16.2 : HBACK= 43.2
WALL MEE3
LAYERS = BÉTON_LOUR PSETH30
THICKNESS= 0.2 0.12
ABS-FRONT= 0.2 : ABS-BACK= 0.2
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 16.2 : HBACK= 16.2
WALL MII1
LAYERS = BÉTON_LOUR PSETH32
THICKNESS= 0.2 0.08
ABS-FRONT= 0.2 : ABS-BACK= 0.2
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 16.2 : HBACK= 16.2
WALL PBTP1
LAYERS = BÉTON_LOUR PSETH30
THICKNESS= 0.2 0.1
ABS-FRONT= 0.8 : ABS-BACK= 0
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 23.8 : HBACK= 0
WALL PBVS2
LAYERS = BÉTON_LOUR FLOCAGE
THICKNESS= 0.2 0.12
ABS-FRONT= 0.8 : ABS-BACK= 0.1
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 23.8 : HBACK= 11
WALL PBEXT1
LAYERS = BÉTON_LOUR FLOCAGE
THICKNESS= 0.2 0.15
ABS-FRONT= 0.8 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 23.8 : HBACK= 64
WALL PIN1
LAYERS = BÉTON_LOUR
THICKNESS= 0.2
ABS-FRONT= 0.1 : ABS-BACK= 0.8
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 23.8
WALL PIN2
LAYERS = LV_FP AIR BÉTON_LOUR
THICKNESS= 0.03 0 0.2
ABS-FRONT= 0.1 : ABS-BACK= 0.8
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 23.8
WALL PH1
LAYERS = LV_FP AIR BÉTON_LOUR PUR
THICKNESS= 0.03 0 0.2 0.20
ABS-FRONT= 0.1 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL PH2
LAYERS = LV_FP AIR BÉTON_LOUR PUR TERRE
THICKNESS= 0.03 0 0.2 0.20 0.08
ABS-FRONT= 0.1 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
WALL CBR
LAYERS = CBR
THICKNESS= 0.001
ABS-FRONT= 0.6 : ABS-BACK= 0.6
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 64
-------------- next part --------------
VERSION 17
*******************************************************************************
*** TRNSYS input file (deck) generated by VMO
*** on ...
*** from TrnsysStudio project: J:\...
***
*** If you edit this file, use the File/Import TRNSYS Input File function in
*** TrnsysStudio to update the project.
***
*** If you have problems, questions or suggestions please contact your local
*** TRNSYS distributor or mailto:software at cstb.fr
***
*******************************************************************************
*******************************************************************************
*** Units
*******************************************************************************
*******************************************************************************
*** Control cards
*******************************************************************************
* START, STOP and STEP
CONSTANTS 3
START=0
STOP=8760
STEP=1
* User defined CONSTANTS
SIMULATION START STOP STEP ! Start time End time Time step
TOLERANCES 0.01 0.02 ! Integration Convergence
LIMITS 150 150 25 ! Max iterations Max warnings Trace limit
DFQ 1 ! TRNSYS numerical integration solver method
WIDTH 80 ! TRNSYS output file width, number of characters
LIST ! NOLIST statement
! MAP statement
SOLVER 0 1 1 ! Solver statement Minimum relaxation factor Maximum relaxation factor
NAN_CHECK 0 ! Nan DEBUG statement
OVERWRITE_CHECK 0 ! Overwrite DEBUG statement
TIME_REPORT 0 ! disable time report
EQSOLVER 0 ! EQUATION SOLVER statement