Matkel,
The fan power is computed from an equation of the form:
pFan = pFan_rtd*(a0 + a1*yFan + a2*yFan^2 + a3*yFan^3 + ... + aN*yFan^N)
where yFan is the fan control signal. If your fan is a simple on/off
(single speed) device then you want to define a0=0 and a1=1. If your fan
is a variable speed device and can have a control signal anywhere
between 0 and 1 then you should set the power coefficients as a0=a1=a2=0
and a3=1. This relationship comes from the fan affinity laws.
Kind regards,
David
On 10/2/2014 05:27, metkell yebiyo wrote:
> Dear TRNSYS users,
>
> I am simulating a GSHP system connected to a 300kW Dry air cooler Type
> 511.
> The Dry air Cooler is controlled when the return temperature from the
> ground reaches 30degC,
> then the Dry air cooler comes on, to maintain the fluid temperature
> going to the ground to 22degC.
>
> My question is, I am trying to obtain the amount of power drawn by the
> fan when the Dry air Cooler is operating. But in order for TRNSYS, to
> calculate the power drawn, you need to put the power coefficients a1,
> a2 and a3, how would I obtain this values? Is it a matter of calling
> the Dry air cooler manufacturer and ask them for this power
> coefficients or what do I need to do please?
>
>
>
> Thank you
> Metkel Yebiyo BEng (Hons), MSc
> CEREB PhD Researcher - Ground Source Heat Pumps
> Room T615
> Department of Urban Engineering
> Faculty of Engineering, Science and the Built Environment
> London South Bank University,
> 103 Borough Road,
> London SE1 0AA
> Tel: +44 (0)20 7815 7639
> E: yebiyom at lsbu.ac.uk <mailto:yebiyom at lsbu.ac.uk>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141002/deb338e5/attachment-0002.htm>
More information about the TRNSYS-users
mailing list