[TRNSYS-users] Fenestration surfaces automatically generated TRNSYS 3D
David BRADLEY
d.bradley at tess-inc.com
Mon Nov 10 09:29:30 PST 2014
Adam,
That is usually an indication that somehow the window that you added
did not get assigned to a zone. I'd recommend that you delete the
windows, make sure you select a zone, then start readding them a few at
a time and importing them into TRNBuild to make sure that they're
getting assigned correctly. It may well be that these are the exact
steps that you are following; I have certainly seen Trnsys3d get into
trouble assigning fenestrations to zones all of its own accord but I
think that deleting them and then importing and saving lots of copies of
the *.idf along the way solved my problem in the end.
Kind regards,
David
On 11/10/2014 11:06, Adam O' Donovan wrote:
> Hi All,
>
> I am using TRNSYS 3D to make a model of a building and recently I have
> entered in the windows and doors on the building. When I reload it
> again the plug-in or sketchup has automatically generated zones for
> each window and called them zones. Below is an example of this.
>
> Can someone explain to me what the issue might be? I am saving
> regularly to the best of my knowledge.
>
> "Error: FenestrationSurface:Detailed, CFD632
> This sub surface is missing its base surface:
> A new zone object has been automatically created for this surface.
> However it is still missing a base surface."
>
> --
> Kind Regards,
> Adam Ó Donnabháin,
> Postdoctoral Researcher,
> CIT,
> *Please, consider the environment before printing this message.*
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141110/90bddfe0/attachment-0004.htm>
More information about the TRNSYS-users
mailing list