Clara,
  Neither of the simple building models (Type12 or Type88) account 
directly for solar radiation gains through windows. In order to account 
for these gains you would need to use a window model (such as Type35 or 
Type687) to account for solar gain and then add those gains into the 
building model using one of the available gain inputs.
Kind regards,
  David


On 3/18/2014 02:43, Clara Stina Good wrote:
>
> Dear TRNSYS users,
>
> I am trying to model a simple building using Type 12c, but I also want 
> to account for solar gains through the building's windows.
>
> My question is if anyone knows of a simple way to do this in a dynamic 
> way, using radiation data from a the weather data reader?
>
> Best regards,
>
> Clara
>
>
>