[TRNSYS-users] Error 118
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Thu Mar  6 09:38:00 PST 2014
    
    
  
Bertrand,
   I have worked on a few building projects that involved cold rooms 
like that. I would recommend that you contact your distributor. It would 
be helpful for them to know which component is running into the error. 
If it is not the building itself but a piece of HVAC equipment it may be 
necessary to use the absolute humidity ratio inputs instead of relative 
humidity because at such low temperatures all of the RH lines in the 
psych chart are collapsing into the saturation line.
Kind regards,
  David
On 3/6/2014 09:48, Bertrand Labedan wrote:
> Hi
>
> I want to simulate a negative cold room (buidling cooled at -4°C).
> In the middle of my simulation I have the TRNSYS Message Error 118 
> about the Subroutine SAT of the utility routine PSYCHROMETRICS.
>
> I don't know how to do avoid this error.
>
> Thanks a lot for your help.
>
> Regards
>
> Bertrand
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
    
    
More information about the TRNSYS-users
mailing list