Sascha,
I do not think that Type567 can be coupled with a window model
(especially not with the Type56 window model since that model relies on
an external data file generated by Window5 and is built into the
building model. I think Type567 would have to be redeveloped as a
combined PV/window model. Short of developing a model I think the best
you would be able to do is to leave the thermal aspect of the window and
the electrical aspect of the window separate. Model the thermal
characteristics as best you can in Type56/Window5. I am also not certain
whether the Type94 or Type194 PV models have ever been tested to see if
they can be used to simulate the performance of PV that is integrated
with a window that also transmits visual light.
Kind regards,
David
On 3/13/2014 02:16, Lindig Sascha wrote:
>
> Dear trnsys users,
>
> I would like to attach a BIPV type 567 in front of a window. It#s well
> explained for the opaque building wall. But I`m not sure how to do it
> if parts of this wall are windows. Has someone already made it like this?
>
> Thanks in advance
>
> Sascha
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140314/8ac87f73/attachment-0001.htm>
More information about the TRNSYS-users
mailing list