Pauline,
with the wall category „INTERNAL“ you have to be very carful.
This option can only be applied for symmetric walls with respect to constructions, convection etc.
In Trnbuild, you have to enter BOTH sides!  If the floor is 5 m * 3 m then you enter 30 m² as area.
[cid:image004.jpg at 01CF809D.603D13B0]
This is the case because the wall is calculated “only half” .
For “ADJACENT” surfaces you enter the area of one side only.
Marion
Dipl.-Ing. Marion Hiller
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Telefon: +49 711 67976-0
http://www.trnsys.de<http://www.trnsys.de/>
Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Stuttgart – München – New York – Paris
Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle
Eingetragen beim Amtsgericht Stuttgart HRB 23347,
Steuernummer: 99073/00911,USt-IdNr.: DE 152272639
________________________________
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von Pauline GELIN
Gesendet: Mittwoch, 4. Juni 2014 08:42
An: trnsys-users (trnsys-users at cae.wisc.edu)
Betreff: [TRNSYS-users] Question about TRNBUILD
Hi,
I have a small question regarding the inclusion of internal surfaces in a zone of TRNBUILD: should we count twice the area of exchange of, for example, an intermediate floor concrete?
Until now, I did not do it because I thought like it was defined as internal it was integrated. And if I counted twice the area I also counted twice the inertia that would be wrong.
Am I right or wrong?
Thanks in advance for your answers.
Best regards,
Cordialement,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image004.jpg at 01CE062A.F4C2C000]
[cid:image006.jpg at 01CE062A.F4C2C000]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com/>
www.woopa.coop<http://www.woopa.coop/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140605/e7f44a98/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 3588 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140605/e7f44a98/attachment-0012.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1718 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140605/e7f44a98/attachment-0013.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1058 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140605/e7f44a98/attachment-0014.jpg>
    
    
More information about the TRNSYS-users
mailing list