[TRNSYS-users] (no subject)
David BRADLEY
d.bradley at tess-inc.com
Wed Jan 15 07:49:23 PST 2014
Ali,
You need to decide what device you want to use to deliver the cooling
to the zone. An absorption chiller generates cold water so you can use
that cold water in a fan coil or (perhaps) in a radiant panel. If you
are using fan coils then you would define a VENTILATION type in
TRNBuild/Type56 that is going to be the air (temperature, RH, and flow
rate) coming from the fan coil model. You'll connect the fan coil model
to pipe models, to a pump model and then to the absorption chiller
model. I would highly recommend that you follow the tutorial called
"Temperature Level Control from Energy Rate Control" located at:
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm
while the tutorial does not specifically deal with absorption chillers,
the process is the same for connecting any kind of air distribution
system to a building.
Regards,
David
On 1/15/2014 00:46, ali javed wrote:
> dear all
>
> i want to cool my building model developed in type 56 by using hot
> water fired single effect absorption chiller type 107 how can i
> connect these two type for cooling purpose ???
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140115/bbbb5cdf/attachment-0001.htm>
More information about the TRNSYS-users
mailing list