[TRNSYS-users] Timebase and Trnsys Message 441
hotline
hotline at Transsolar.com
Thu Feb 6 00:25:21 PST 2014
Dear Eva,
the best choice of the time base is:
time base = time step
However, this isn't always possible and you'll receive an error message.
The step of temperature is related to that fact that the time base is larger then the simulation time step. When the wall history is updated based on the time base a step might be encountered.
For control it is recommended to use a component with hysteresis like
Type 2 and NOT Equations. The "freezing" indicates that a lot of iterations
are performed at this time step in order to reach convergence.
You should set the max. number of iteration to a considerable number
like 50 and improve your control in order to achieve convergence.
Marion
Transsolar Software Team
-----Ursprüngliche Nachricht-----
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von eva.zacekova at fel.cvut.cz
Gesendet: Mittwoch, 5. Februar 2014 12:56
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Timebase and Trnsys Message 441
Dear all,
I have built a small one-zone building with ceiling heating (active
layer) in Trnsys, however, its behavior looks a little bit strange to
me.
The first problem is that I am not sure about setting of the timebase
in building editor. The U-values of external walls are 0.668 while the
thickness is 0.225. What timebase would you suggest? I tried several
different values (0.25, 1, 1.5). With 1 and 1.5, the time profile of
the zone temperature was somehow stairs-like (fast rising at the
beginning of the sampling period and hardly changing at the end of the
sampling period; the sampling period is 15 minutes). With 0.25, the
zone temperature profile was changing very slowly. In trnbuild manual,
I have found that the higher timebase value, the "slower" the behavior
is - however, this does not correspond to the behavior of the building
I have built. Do you have any suggestions/advices for me?
The next problem is with the heating signal. I consider that the
active layer is placed in ceiling. In case that the heating signal is
not very smooth (the temperature of the heating water is changing
rapidly), the simulation gets stuck (and it also gets much slower) for
and in the list file, the following Trnsys Message occurs:
"TRNSYS Message 441: The inputs to the listed units have not converged
at this timestep. The values at the last iteration will be used and
the simulation will proceed."
Is this message related to the fast changes of the heating water? Can
I solve the problem of freezing simulation while preserving the fast
changes of the heating water?
Thank you very much in advance.
Best regards,
Eva
--
Dipl. Ing. Eva Žáčeková
Czech Technical University in Prague
Faculty of Electrical Engineering
Department of Control Engineering
Prague 2, Karlovo náměstí 13, E-21
+420 22435 7689
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
More information about the TRNSYS-users
mailing list